Someone has told you the heat exchanger is cracked, or put a red tag on your furnace and shut it off. Now you're looking at a few thousand dollars and you have to decide fast. Before you do, get it checked by someone who isn't selling you the furnace.
A furnace red tag second opinion is our regular $149 diagnostic. We're a G2-licensed, TSSA-registered contractor. We test the furnace ourselves and show you what we find. If it really does need replacing and you buy the new furnace from us, the $149 comes off the price.
We get a lot of calls from people who were told their heat exchanger is cracked when it isn't. We also red-tag furnaces ourselves when the numbers call for it. Either way you'll see the readings.
While you wait: don't relight or run a furnace that's been tagged and shut off. If you smell gas, leave the house and call Enbridge Gas's emergency line or 911 from outside.
What a furnace red tag means in Ontario
A red tag is a gas safety notice from a licensed gas technician. There are two kinds.
- Immediate hazard (often called an A tag). The gas to the appliance is shut off on the spot and stays off until the problem is fixed.
- Not an immediate hazard (a B tag). You get a deadline, typically 30 days, to repair or replace the appliance before the gas utility shuts it off.
In both cases the utility is notified, and the tag has to be cleared by a licensed contractor once the problem is corrected.
Two very different reasons for a tag
A cracked or failed heat exchanger. This is the one worth a second opinion. It's a judgment call based on testing, it's expensive, and it's one we often find was wrong.
A code or safety violation. A leaking gas valve, a venting problem, something installed wrong. There's nothing to argue about here. It has to be corrected. We do the repair and get the tag cleared.
How we check a heat exchanger
We don't go by a glance. We test.
- Gas pressure. Set and checked against the manufacturer's specification.
- Combustion analysis. A flue gas analyzer samples what the furnace is actually producing: carbon monoxide, oxygen and carbon dioxide. Ours goes out for calibration every year.
- Burners and air-to-gas ratio. Cleaned and adjusted if they need it, then tested again.
- Camera. We look inside where a camera can reach.
If the gas pressure is right, the air-to-gas ratio is right, the burners are clean and the furnace is still reading high carbon monoxide, something is wrong with the heat exchanger. At 100 parts per million or more in the flue, we treat it as failed and unsafe to run. On a new, properly set up furnace we typically see somewhere between 8 and 20.
You see the numbers. If they're fine, we tell you they're fine.
What happens next
If the heat exchanger is fine, we tell you so and fix whatever was actually wrong, if anything. If there's a tag on the furnace, we get it cleared.
If it has failed, you have two options. Replacing the heat exchanger out of warranty is $2,000 to $3,000. Even when the part is covered under warranty, the labour is generally $1,000 to $1,500, because the whole furnace has to come out and be stripped down. After all that you still have old motors and old controls around a new heat exchanger. So in most cases we recommend a new furnace at $3,400 to $5,400 installed, and your $149 comes off the price. It's still your decision.
Clearing the tag with Enbridge
Once the repair or replacement is done, we send the tag in to Enbridge Gas for clearing. We do this for both A tags and B tags, so you're not left chasing paperwork to get your gas back on.
Why a furnace second opinion is worth it
A repair doesn't bring in as much in one visit as a new furnace does. So some technicians stretch the truth. You need an igniter and a flame sensor, and you get quoted a gas valve and a control board too. Or you're told the furnace is finished on the coldest weekend of the year, when you can't shop around.
Here's one from a commercial rooftop unit. A business called us for no heat. The contractor before us had said the control board needed replacing, which with labour would have run $1,100 to $1,200. On the roof we found the heating wire disconnected. We reconnected it and the unit still wouldn't start, because the inducer motor wasn't running. The wire that powers the inducer had been unplugged from the ignition control board as well. We plugged it back in and the unit fired right up. We checked the carbon monoxide, it was well within the normal range, and there was nothing wrong with the unit.
We've had the same thing with "your heat exchanger is cracked" and with "you can't get parts for a furnace that old." We go, we check, and sometimes it simply isn't true.
We don't use pressure tactics. We'd rather keep a customer for years and sleep at night than sell one furnace that wasn't needed. We wouldn't want it done to our own families, so we don't do it to yours.
And when the tag is right
Sometimes it is. A furnace can heat the house just fine and still be one that has to be shut down, because a failing heat exchanger doesn't give you a warning before the day it gets dangerous. If our readings say the same thing the first company did, we'll tell you that too, show you why, and lay out your options.
Where we work
Toronto and the GTA, including Scarborough, North York, Etobicoke, East York, Markham, Vaughan, Richmond Hill, Mississauga, Aurora and Newmarket, and east to Pickering, Ajax and Whitby. For the right job we'll go farther, up to about two hours from Toronto. Call and ask. See our service area for more.
Red tag and second opinion questions
How much is a furnace second opinion in Toronto?
It's our regular diagnostic: $149 plus HST, or $199 after 6 pm and on weekends. If the furnace does need replacing and you buy the new one from us, the diagnostic fee comes off the price.
My furnace was red-tagged for a cracked heat exchanger. Can you check it?
Yes. We check the gas pressure, run a combustion analysis with a calibrated flue gas analyzer, and look inside with a camera. If carbon monoxide in the flue is under control and everything else checks out, the heat exchanger is doing its job. At 100 parts per million or more, we treat it as failed. You see the readings either way.
Can you remove a red tag from my furnace?
Once the problem is corrected, yes. We do the repair or replacement and send the tag in to Enbridge Gas for clearing, for both A tags and B tags. If the tag is for a code violation like a leaking gas valve, it has to be fixed first. A tag can't just be taken off.
What is the difference between an A tag and a B tag?
An A tag means an immediate hazard, and the gas to the appliance is shut off right away. A B tag means the problem isn't an immediate hazard, and you get a deadline, typically 30 days, to repair or replace the appliance before the gas utility shuts it off.
Can a cracked heat exchanger be repaired?
It can be replaced, not patched. Out of warranty that's $2,000 to $3,000. Even with the part under warranty, labour is generally $1,000 to $1,500. Because the rest of the furnace is still old, we usually recommend a new furnace at $3,400 to $5,400 installed instead.
Is it safe to run my furnace while I wait for a second opinion?
No. If it has been tagged and shut off, leave it off until a licensed technician has tested it. If you smell gas, leave the house and call Enbridge Gas or 911 from outside.
Been told you need a new furnace? Call (647) 269-9704 before you sign anything, or send us a message with a photo of the tag and what you were told.